Hello Alpha Paolo, You can change the supply system voltage to any of the selectable levels by two different methods. First for default use upon opening tool: In menu upper select Tools / Options / Supply System Preassignment then use pull down menu to choose 400 Volts 3 Phase. Then Check box for "Allowance for supply voltage differing from the rated voltage". Enter 360 Volt for Lowest Supply Voltage Next within an open project itself in partial view of Drive Systems: Right Click on Supply System Properties then left click on "Open Object". Choose 400 Volts 3 Phase. Then Check box for "Allowance for supply voltage differing from the rated voltage". Enter 360 Volt for Lowest Supply Voltage Attached is a view of screens. Deputy AttachmentC:\Documents and Settings\summrl\My Documents\FY12\Reference\Forum\SIZER Supply\SIZER Supply.jpg (638 Downloads) |