Hello, I have Problem in Profibus network That plan is in The following PROFIBUS NETWORK.jpg This profibus network have a lot of noise and when occurs The problem in a station , All the segments become in trouble Due to data transfer rate in network , 12 Mbit / s , the profibus cable length is too long (371 meter) Please help me To solve the above problems and for isolate different parts of each That the problem in one segment can not cause problems in other segments... plan with all nodes is in The following full profibus plan.jpg Do below idea is appropriate ? New Design.jpg Please guide me Thanks Best Regards |
Control & Instrument Engineer |
|
9/11/2013 7:38 PM | |
Posts: 8946 Rating: (999) |
Reduce speed to 1.5 M AND use repeater! |
9/12/2013 7:36 AM | |
Posts: 8946 Rating: (999) |
Check: All cables OK? Als shields connected in propper way? Resistorswitches in right position and working? NO segment with more 32 Slaves AND NOT longer than 50m without repeater! Have a look here: http://www.indu-sol.com/en/index.html and also search for "Profibus inspector" Last, but not least, shoot the guy who select 12M for this topology. |