6/7/2011 6:59 AM | |
Joined: 10/7/2005 Last visit: 11/19/2024 Posts: 3027 Rating: (1057)
|
Hello blitzenau you do NOT enter the registration key value into the MODBUSPN block itself. Instead, you assign theregistration key value(stored in a String in a DB) as the Input parameter"REG_KEY” of the MODBUSPN block when you call it. |
Cheers |
|
6/7/2011 7:59 AM | |
Joined: 10/3/2008 Last visit: 8/28/2024 Posts: 961 Rating: (124) |
Hi, have a look at the example project. Here you can see how to configure. Wüstenräuber |
6/8/2011 4:04 AM | |
Posts: 691 Rating: (37) |
REG_KEY is the License Number on the Siemens Packet for Open Modbus. |
6/8/2011 8:56 AM | |
Posts: 12 Rating: (1) |
The Licence No. on the package is sent to Siemens to get the Reg_Key. They are different. |
6/8/2011 9:19 AM | |
Posts: 3093 Rating: (323)
|
Hello Shar, |
6/8/2011 9:58 AM | |
Joined: 10/3/2008 Last visit: 8/28/2024 Posts: 961 Rating: (124)
|
The IDENT_CODE + the license no. from the box... Then you get the REG_KEY. |
2/9/2015 3:39 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
|