Hello Everybody, Can someone help me with the following issue? In a PCS7 V8.2 CPU 410-5H I want to connect some 3° party devices through ModbusTCP using the integrated ports in the CPU and I´m not sure what is the right license to do it Can someone tell me if the 2XV9450-1MB02 is the right MBLF? Gustavo ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 5/13/2016 12:48:21 PMNew subject after splitting |
|
5/13/2016 1:43 AM | |
Joined: 9/27/2006 Last visit: 10/11/2024 Posts: 12287 Rating: (2685) |
Hello Gustavo; Are you planning to use your H-CPU as standalone or redundant operation? Your selected part number is correct for a stand-alone, non-redundant CPU. For a redundant system, you would need Modbus/TCP PN RED, 6AV6676-6MB10-0AX0. See the attachment, taken from the following FAQ: Which technical data applies for the SIMATIC Modbus/TCP blocks and for which CPUs and CPs is it released. https://support.industry.siemens.com/cs/ww/en/view/104946406 Hope this helps, Daniel Chartier |