Thank you guys, but the first problem was that I had a problem with the optic fiber connectors, they wore not from siemens, and after that I sow that the software firmware of the CPU was not the same for both, one of them was on the V 6.0.6, and the other one was V 6.0.4. After that I received the correct conectors I've made a factory reset for both of the CPU and after that I sow that the software firmware was different. To do a factory reset you have the instructions in the CPU manual at page 75, or you could download the attachment. To control the software version of the CPU you have to go to: and you downloadit from: I hope that it helps. AttachmentReset_CPU.zip (502 Downloads) |