... and have I not expected this response? I wonder why Siemens even bother to have forum like this at all. |
7/19/2016 5:04 PM | |
Joined: 4/28/2015 Last visit: 7/19/2016 Posts: 3 Rating: (0) |
How about a RIB1C relay? |
11/15/2016 3:31 PM | |
Joined: 11/15/2016 Last visit: 7/28/2017 Posts: 1 Rating: (0) |
A couple years back I tested the ability to define the “super Universal” points on our PXC Compacts as LDO’s. I used the following Functional Device Relay: RIBME2401B Apparently when the “super Universal” points on the PXC-24 (X13, X14, X15, or X16) are defined as LDO’s the put out around 23 VDC. When coupled with a special “low Coil Input” relay, you can expand the amount of DO’s available on the Compact. Note: The original PXC’s did not have “ Super Universal “ outputs… Check your hardware before trying this solution. I used the attached relay and set it up as an LDO and a L2SL Point and they both worked fine. The only issue is you have to provide 24vac to the relay for supply power. Thanks John Stoddart AttachmentRIBME2401B.pdf (1028 Downloads) |