Hello CERSKYTECH, Since you have chosen WinCC RT Advanced, you shall know that you cannot configure H system in TIA, so you will use Step 7 software for H system and WinCC Advanced for PCs Runtime So you will need to use "Device Proxy PLC" to be able to have a combined configuration |