Hi I have a simple project using a pressure sensor with a on and off set point ( see attached software ) The system has two pumps one duty and one standby circulating the water at set-point 1 and then on demand set-point 2 I want to do the following within the project. 1. If the pressure drops below a certain set point then the inverter drive will ramp up from its set point to then maintain the pressure returning to its set-point 2. if the duty pump cant maintain the pressure the standby pump will kick in and then fetch the pressure back to it required set-point Thanks Andrew
AttachmentPressure.zip (160 Downloads) |
2/22/2018 10:29 PM | |
Joined: 12/18/2014 Last visit: 2/19/2025 Posts: 34714 Rating:
|
Like this (see attachment)? Or something else?
AttachmentPressure_V2.zip (184 Downloads) |
2/22/2018 10:51 PM | |
Posts: 200 Rating:
|
Sorry for some reason i can't open the file |
2/22/2018 10:58 PM | |
Joined: 12/18/2014 Last visit: 2/19/2025 Posts: 34714 Rating:
|
I make it new with LSC V8.1.1. Try to open.
AttachmentPressure_V2.zip (193 Downloads) |