(1)| 3/29/2019 10:21 AM | |
|
Posts: 4 Rating:
|
Can the Logo 230RC be connected directly to the AM2 RTD module? Thankey. |
| 3/29/2019 10:29 AM | |
|
Joined: 12/18/2014 Last visit: 12/27/2025 Posts: 36378 Rating:
|
Yes it's possible. But then no 230V extension modules can be connected to the AM module. See attachment. AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 pages 33+34.pdf (386 Downloads) |
| 3/29/2019 11:33 AM | |
|
Posts: 4 Rating:
|
The AM2 RTD needs 24 Vdc of power. What I do not understand is where to get that voltage from the Logo 230RC, without using the Power Logo. Thankey. |
| 3/29/2019 11:35 AM | |
|
Joined: 12/18/2014 Last visit: 12/27/2025 Posts: 36378 Rating:
|
You need an own 24VDC power supply. The power supply does not from the base module. |