7/4/2019 9:23 AM | |
Posts: 80 Rating: (1) |
Hi Beevee, Thanks for your reply. Attached is existing connection. |
7/4/2019 9:37 AM | |
Posts: 80 Rating: (1) |
Hi BeeVee, Regards to earlier system overview, I miss a Scalance X101 media converter in between PC WinCC to H1 bus. On that PC, it using CP1613. |
7/4/2019 10:59 AM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating: (91) |
Hi azad_dsc, I would suggest the following: https://www.blackbox.com/en-us/store/Detail.aspx/Media-Converter-Ethernet-AUI/LE180A Use some of these convertors and get rid of thick H1 cables. WinCC can communicate over standard ethernet card also. No need for CP card in PC. For each connection in CP1430 you need to program a new connection in S7. Keep in mind that Fetch Active is not possible in S7.You can choose between send/recv, fetch passive and write passive. Maybe you should consider conversion to TIA in stead of S7-400. If you don't want to replace thick H1, tranceivers and drop lines, you can use the media converting switch that you suggested. Kind regards, |
This contribution was helpful to1 thankful Users |
9/18/2019 11:13 AM | |
Posts: 80 Rating: (1) |
Hi Guys, Continue the same question as above, the existing CP1430 connections have been listed and as attached. As we upgrade S5 to S7 rack, So each connection to the same ethernet address need to be configured in Netpro? Azad AttachmentCP1430 Connection detail.xlsx (273 Downloads) |
Follow us on