(0)| 9/15/2019 12:11 AM | |
|
Posts: 16 Rating:
|
i asked if i can access to starter through MPI PLC connection (routing) s7 300 |
| 9/15/2019 5:39 AM | |
|
Posts: 8092 Rating:
|
Which device you want to access via STARTER on MPI? Drive - yes. PLC - No. |
| 9/15/2019 8:54 PM | |
|
Posts: 16 Rating:
|
i'm already online on PLC by MPI connection,i asked if i can access to drives also(starter) |
This contribution was helpful to
|
|
| 9/16/2019 10:05 AM | |
|
Joined: 8/31/2005 Last visit: 12/16/2025 Posts: 2198 Rating:
|
The drives must be under the S7-CPU in SIMATIC Manager. If they are on the same level as the S7-CPU you need Drive ES. Then setup the routing: https://support.industry.siemens.com/cs/ww/en/view/2383206 In Starter you have to change the online interface to S7 (not DRIVE). |
|
|
|
This contribution was helpful to
|
|
| 9/16/2019 8:47 PM | |
|
Posts: 16 Rating:
|
thanks in advance it's really useful link,i will try it and revert with feedback |
| 9/29/2019 10:31 AM | |
|
Posts: 16 Rating:
|
other photo |