Hello combinu, teststop is required to be performed at least once a year to ensure integrity of the STO functionality. When talking about the G120C with safety integrated basic functions a teststop is performed each time you select a STO, which resets the timer to its initial value. More detailed information about the teststop could be found in the G120 safety integrated manual, section 5.10.3 https://support.industry.siemens.com/cs/ww/en/view/109757227 Check out the following SIOS link to deactivate the diagnostic request https://support.industry.siemens.com/cs/ww/en/view/109486142 There are some tuturials available which are also mentioning the safety commissioning/parameter setting on the G120C. https://www.youtube.com/watch?v=xh8JTO2hgIQ |
With best regards, |
|
12/19/2019 10:49 AM | |
Joined: 5/26/2017 Last visit: 1/20/2023 Posts: 20 Rating: (0) |
Tried it also but still i get an incorrect current password when i try to start SI commissioning |
12/19/2019 11:25 AM | |
Joined: 5/26/2017 Last visit: 1/20/2023 Posts: 20 Rating: (0) |
Thanks for your help. We will see what we can do from here. Best Regards and Happy Holidays |