3/29/2020 7:46 PM | |
Joined: 10/3/2019 Last visit: 12/6/2024 Posts: 11 Rating:
|
Hello, thanks for the reply!! If you see any problems in the program please tell me. Really a lot of thanks!! Attachmentgrup_pompare_viseu_de_josl_V2_0BA8.Standard.zip (141 Downloads) |
3/29/2020 8:29 PM | |
Joined: 12/18/2014 Last visit: 2/20/2025 Posts: 34727 Rating:
|
You must set in your case the OFF parameter of the block B002 by a value of -62. That's 3 mA. And you must connect all outputs of all blocks to a input of a other block, or to a open connector, or a flag or a output. By analog blocks to a input of a another analog block or a analog flag or a analog output. In simulation you must do this not. Attachmentgrup_pompare_viseu_de_josl_V3_0BA8.Standard.zip (149 Downloads) |
3/29/2020 9:52 PM | |
Joined: 12/18/2014 Last visit: 2/20/2025 Posts: 34727 Rating:
|
Make it so.... See attachment... |
3/29/2020 10:03 PM | |
Joined: 10/3/2019 Last visit: 12/6/2024 Posts: 11 Rating:
|
THANK YOU!!! |
This contribution was helpful to
1 thankful Users |
3/29/2020 10:05 PM | |
Joined: 12/18/2014 Last visit: 2/20/2025 Posts: 34727 Rating:
|
That sounds good ... |