Hello, I have the same problem. Alarm 21612 and along with this comes others such as: 700020 monitoring module not ready ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 03/12/2021 11:19:09New subject after splitting |
|
3/14/2021 2:13 AM | |
Joined: 10/17/2007 Last visit: 9/17/2024 Posts: 4031 Rating: (353)
|
1st of all--please in the future--post alarm # and alarm text as well , also give a more detailed story, such as your machine running good yesterday this morning when you run the program,...... 2nd --I attached Alarm 21612 help from another member --also it is in Siemens manual "Diagnosis" if you read this file--you will see how important you post-alarm text 3rd--you have Machine builder alarm 700020 monitoring module not ready That help you to find the problem easily --check or replace the "Monitor module" --if you don't know which is it. check the machine electrical drawing or post a picture of your drive system --you need post the whole drive modules --I think your monitoring module should in the place of # 5 or # 6 from the left
|