Please change the battery as specified in the attachment. Do not take care about the data inside- they're already gone... (message: "Defaults loaded") After the battery's replacement You need to cancel the NC/PLC-memory and reload the NC-& PLC-archive. Please note: All modified data in between the creationing the archive and Your latest successfull operation at the machine are gone! (PartPrograms, ToolData, Offsets....) hopt that helps CNC600 Attachmentbattery replacement CCU.pdf (578 Downloads) |
hope that helps |
|
8/20/2010 10:17 AM | |
Joined: 10/27/2009 Last visit: 3/15/2024 Posts: 455 Rating: (77) |
Ofcourse it's difficult to decide from far away to suggest You to order a service engineer or to try to solve by yourself. Just read my comments and check it out by yourself.
Before You start these actions make sure You've got: (1) a new battery and (2) the NC/PLC archive(s) Check the controls and displays of CCU at page 5-39 (attachment) Please follow this order: (status check) - check the LED's H1/H2 If only GREEN LED lit - it's OK, the further cancellation of NC-Memory and PLC-Memory is not really necessary. goto "reload archives". Otherwise follow the next instructions. (Cancellation NC-Memory) - set rotary switch S3 to position "1" and press "S1" (or PowerOFF/ON the entire system) - wait until the 7-segment-LED is in status "5" or "6" (pending on the PLC-status) ==> NC-memory was cancelled successfully - set rotary switch S3 back to position "0" !!!!!!!!!!!!!!!!!!! (Cancellation PLC-Memory) - follow the instructions from page 5-43 (frequently manipulation of S4) ==> PLC-memory was cancelled successfully After this procedure the green LED's in H1 and H2 should lit. (Restore the archive) - Set Rotary switch S4 to position "2" (STOP) - Select on HMI-screen the "Start-Up"-screen - Enter the password SUNRISE (finally: manufacturer-access is setted) - Select on HMI-screen the "Service"-screen - load the saved NC-archive - load the saved PLC-archive - Set Rotary switch S4 to position "0" (RUN) - Power OFF/ON the entire System ==> reloading of archives was successfull if the green LED's in H1 and H2 lit. Now You should check the data in he CNC (ToolData....) Ofcourse there can occure other obstacles during this process as well, but I think You can try this sequence. You find additionaly information in the attached document. hope that helps CNC600 AttachmentStartUp.pdf (535 Downloads) |
hope that helps |
|
8/20/2010 12:26 PM | |
Posts: 15 Rating: (0) |
Thank you very much for your help |
8/23/2010 2:28 PM | |
Posts: 15 Rating: (0) |
New battery will be here tommrow does any one know where i can get the NC/PLC archive (s)? Best regards Craig |
8/23/2010 2:57 PM | |
Posts: 15 Rating: (0) |
Scratch that Ive just found the back up disc, is there a guide for locating and initialising the backups ive found one for creating them? |