3/30/2017 3:51 PM | |
Joined: 9/27/2006 Last visit: 5/25/2024 Posts: 12257 Rating: (2668) |
Hello Leinad; I hope I understand your question correctly: IO-link by itself only has cyclic exchanges with the slaves on its network. However, in Siemens' world, IO-Link masters are a subnet from a Profibus-DP (or Profinet) network, and the DP master/Profinet IO-Device uses acyclic exchanges to parametrise the IO-link master. Please study this FAQ for more details: Acyclic Read and Write with the IO-Link Library Hope this helps, Daniel Chartier |
3/31/2017 2:41 PM | |
Joined: 9/27/2006 Last visit: 5/25/2024 Posts: 12257 Rating: (2668) |
Hello Leinad; My (very small) experience with IO-Link masters and devices, both from Siemens and other controller families, reveal no conscious connection to M-sequences on an IO-link device though programming. M-sequences codify the data exchanges between the device and the master, and I believe they are completely integrated in the IODD file of the IO-Link device that you load into the master at configuration time. They then become transparent to the user and are part of the cyclic data exchanges. The IO-Link libraries provided by Siemens are used to acyclicly read and write parameters to the IO-Link master and the devices through function blocks provided by Siemens. You can also use them to read diagnostics from the IO-Link devices upon request (though function block calls). See the following documentation: IO-Link System manual v3.0 (Complete edition) Hope this helps, |
Last edited by: dchartier at: 3/31/2017 2:44:24 PM |
|
This contribution was helpful to1 thankful Users |