10/30/2020 8:33 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (873)
|
Hello, For Emergency 3000 alarm check bleow points. 1. Check DB2.DBX180.0, it must be 0. Please select MENU button on OP, press DIAGNOSIS ---> press PLC ----> PLC STATUS window will pop up. In first raw type DB2.DBX180.0 & check its status. If it is 1, it is the reason emergency alarm 3000 alarm to pop up. To trouble shoot this you need to go online with PG/PC having SIMATIC manager Step 7 v 5.4 software & MPI cable. If you do not have software & haradware, check the ladder or document supplied by OEM. In the ladder logic check the network in which DB2.DBX180.0 is set. This will help to trouble shoot. 2. In electrical circuit diagram find out 2Q3 circuit breaker & check its application. It might be for protection of auxiliary motors like chip conveyor, coolant motor etc. etc. Also check the auxiliary control NO, NC & find out where are they connected in electrical circuit. This might be input to PLC. But generally such overload protections are not connected as Emeregency STOP unless & until it is related with safety issue.
Please refer file attached to user pandora303 post, emergency stop acknowledge or rest only when DB10.DBX56.1 (Emergency stop button pressed), DB10.DBX106.1 (emergency stop is active i.e. bit is set which should get released after releasing of PB or any saftey device) these two signals are low & when reset key i.e. DB21.DBX7.7 is pressed i.e. its signal changes from low to high & again to LOW after releasing key. So check these signal status on PLC STATUS page. |
Last edited by: PISCEAN 2010 at: 10/30/2020 09:51:34Emergency sequence expalined |
|