3/8/2016 8:21 AM | |
Posts: 30 Rating: (0) |
this is diagram for X axis |
3/8/2016 8:22 AM | |
Posts: 30 Rating: (0) |
This is for Y axis |
3/8/2016 8:31 AM | |
Posts: 30 Rating: (0) |
this is Z axis |
3/8/2016 8:33 AM | |
Posts: 30 Rating: (0) |
This is last axis, W axis |
3/8/2016 10:04 AM | |
Joined: 12/9/2015 Last visit: 3/28/2022 Posts: 4 Rating: (0) |
AS1_X=0V AS2_X=0V AS1_Y=0V AS2_Y=0V AS1_Z=0V AS2_Z=0V AS1_W=0V AS2_W=0V |
3/8/2016 10:11 AM | |
Posts: 30 Rating: (0) |
Dear Piscean, Please take alook to my attachment for Schematic of AS1-AS2 series |
3/8/2016 11:28 AM | |
Posts: 30 Rating: (0) |
Dear Piscean, do you have full specification of 34 pins RIBBON cable? Thanks |
3/8/2016 11:59 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please see attachment.
Ok. Just power On the machine, press cycle start button & measure the analog in put voltage by multi-meter, with DC voltage range, at X, Y, Z, W axis module (which ever is applicable) card at terminal at X321 terminal 56 & 14. Ensure that feed pot on CNC panel is at 100%. Please reply on measurement of actual DC voltage at LT power module bus. Attachment611A_RIBBON_CABLE_DATA (1).pdf (340 Downloads) |
3/8/2016 1:47 PM | |
Joined: 12/9/2015 Last visit: 3/28/2022 Posts: 4 Rating: (0) |
DC bus voltage is 572V. |
3/8/2016 1:54 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
OK. Please provide set point to axis externally & check the behaviour of axis motor. (As suggested in earlier post) |