3/30/2017 10:55 PM | |
Posts: 20 Rating: (1) |
|
3/30/2017 10:57 PM | |
Posts: 20 Rating: (1) |
|
3/30/2017 10:58 PM | |
Posts: 20 Rating: (1) |
|
4/4/2017 1:56 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello Lekso Tsitsishvili, From the 2nd screen shot, it signifies, axis 3 NC OFF1 & pulse enable signals are missing. In the same screen axis 4, pulse enable signal is missing. Please check the logic for these missing signals. Since those are missing, drive goes in fault mode, infeed module signals are cutt off & that is how X & Z axes also stops working. HTH. |
4/4/2017 2:37 PM | |
Posts: 20 Rating: (1) |
Hello, All signals are enabled for the each axis. But for axis AX3 and AX4 Off1, control enable and pulses enable signals are blinking. |
4/6/2017 2:24 PM | |
Posts: 20 Rating: (1) |
Hello, The problem was a PLC logic and I have just fixed it. Thanks for your helping. |
This contribution was helpful to1 thankful Users |
1/30/2018 8:59 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872)
|
Hello chuot_bac, Please check if NC, PLC communication is established, the staus of 7 segment display on NCU box, please check PLC logic, infeed module pulse enable, drive enable commands are ON. Check the axes configuration. HTH. |
1/30/2018 9:11 AM | |
Posts: 20 Rating: (1) |
Hi, In my case DC screws on S120 modules were not enough tightened. After tightening the fault has disappeared immediately. |