8/31/2005 12:14 PM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating: (32)
|
regarding to your questions to the address setting in the ET100: 1) The high-speed counter card 6ES5 385-8MB11, for example, has an address setting like an analog card. In the ET100, it has the address setting "2AX" The counter card 6ES5 385-8MA11 has in the ET100 the address setting "4DX". 2) The address area is usually in the P-area, but it can be also in the Q-area. 3) It is not possible to have the same addresses for different cards. The cards in the main rack and in the ET100 racks must have diffferent addresses. I think, you should write the addresses for the ET100-cards regarding to the following tips: - You have a wiring diagram of the ET100, where is written the address of the card - You look into the program of the CPU, which input-address and output-address is called - You look into the "Assignment List" of the program, if this list exists. The address setting for the ET100, the EPROM in the IM308-card, you must program with the software "COM ET100". The manual of the ET100 you find with the ID-number "14780953" The manual of the COM ET100 you find with the ID-number "14780735" On the Internet: http://www.siemens.com/automation/service&support Best regards Your Technical Support for Automation & Drives SIEMENS AG |
Last edited by: CS Moderator at: 10/12/2005 1:30 PMLast edited by: CS Moderator at: 10/12/2005 1:30 PMLast edited by: Import-User-2 at: 9/15/2005 3:25 PM |
|
4/23/2015 12:54 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating: (123) |
New question by neththi published twice. You can find the second thread with the subject Communication error (S5 -115 U) -308-3UA12 Expansion Unit interface module and et 100u.
|