12/14/2018 2:22 PM | |
Posts: 1 Rating: (0) |
Dear All, I have to configure 4-20mA level sensor in trapezoid shaped container to give me continuous increase in liquid quantity with respect to time. The flow is 10l/min in container, i know time require to fill the container. but i want to know how much liquid is in side with each 4mm increase in sensor height As the increase of level sensor height =4mm is different as in the top of trapezoid container level sensor gives me the value with 4mm increase in liquid height please find the shape of container in attachment Thank you ------------------------------------------------------------------------------------------ AttachmentContainer.pdf (33 Downloads) |
Last edited by: Jen_Moderator at: 12/17/2018 7:07:35 AMNew subject after splitting |
|
12/15/2018 5:20 PM | |
Joined: 5/6/2010 Last visit: 6/2/2024 Posts: 1966 Rating: (274) |
Hello, you can find at the attachment a calculation for your tank, based on a truncated pyramid. You must calculate all the values in the PLC with easy formulas. e.g.
Hope this is helpful. regards Attachmenttank_volume.pdf (32 Downloads) |