8/5/2009 2:20 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
hello, i think there is no way. You can use in Step5 Documentation -> I/Q/F-List and compare it with the nr of existing I/O cards and the assignment list. Regards
André Räppel --------------------------------------------------------------------------------- www.raeppel.de work faster withinnovative PLC-Tools |
8/6/2009 3:24 AM | |
Joined: 10/7/2005 Last visit: 5/2/2024 Posts: 3004 Rating: (1046) |
Hello yac Further to André's advise, check too if an I/O address list has been configured in DB1 (DB1 address lists can be used for single CPU's and must be used for multiprocessing). If so, it will (must) have all existing (Digital) I/O addresses in it (for the processs Image address range 0-127). If not,you can of course alsotake out each I/O card and check its DIP switch basedaddress to be sure to be sure. I hope this helps |
Cheers |
|
8/6/2009 8:45 AM | |
Posts: 8946 Rating: (999) |
One thing more: |
8/6/2009 1:38 PM | |
Posts: 31 Rating: (0) |
Hello, Thanks for your advice, but how to find out if I am using the Q area in the central rack? Best regards |
8/6/2009 4:48 PM | |
Posts: 8946 Rating: (999) |
Checking the DIP - switches. |
8/10/2009 3:06 AM | |
Joined: 10/7/2005 Last visit: 5/2/2024 Posts: 3004 Rating: (1046) |
Hello again yac (memory) address F F080hex corresponds to PIB128 (IB0 is ataddress F F000hex). Not too sure how this info will help you though (using the absolute memory address to accessthe I/O'sis rarely done).
As per previous advise, the one and only safe way is to check the DIP switches on every card (which does unfortunately require you topower off the S5). I also agree with Juergen (IBN Service) that Bhaskaran "checking method" can be fraud with danger andwould strongly advise you to only consider using it when the Plant/machine is NOT running and safely isolated! The main reason for this is that you can not "trust" the I/Q/F list to contain all used I/O's! For one, a 32 channel DQ card with for example start address 32 mayhave the last two bytes unused by the program. If you now relyONLY ontheI/Q/F list, you would falsely assume that QB34 & 35 are free. The second (and moreimportant reason)is the due to indirect addressing which - if done in the logic - will "hide"the indirectly addressed I/O's from the I/Q/F list. I don't know if indirectI/O addressing is used by your program, but it is something to be aware off. I myself used I/O address listDB's and indirect I/O addressingquite frequently in the good old S5 days due to the need for for(OperatorTank number based selection) flexible control ofFermentation and Storage cellars transfer and cleaning programs. Also, Analogue input reading and scalingrelied more often than not on indirect addressing (even the Siemens S5 standard blocks used the "BG" and "KNKD"values rather than "real" I/O addresses). In sums: If you want to be sure, check the DIP switches of the cards. If you can't do so for whatever reason, make sure that the I/O/F list based used I/O's "line up" fully with the number and density of the used I/O cards andcheck too if you canget hold of electrical schematics which may contain card addresses. I hope this helps |
Cheers |
|
8/10/2009 10:24 AM | |
Joined: 10/7/2005 Last visit: 5/2/2024 Posts: 3004 Rating: (1046) |
I start to wonder if you intend to use the FB IM308C (default number is FB 192) which would also explain why you previously asked for the "address area". Anyhow, usage of this FB192 is optional (I never had the need for it), but if you do want to employ it, the default IM308C/FB192 "DPAD parameter"address is (F)F800 and can be changed in the Master propertiesfrom your COM Profibus cofiguration. This address however has nothing to do with your ET200M I/O addresses, which are configured on the DP Slaves. Attached is an example screendump of it which shows P area I/O address assignment. |
Cheers |
|
8/10/2009 2:27 PM | |
Posts: 31 Rating: (0) |
Hi fritz, Thanks a lot for your help. First of all I do not want to use FB192. Second, I investigated the actual condition of the PLC as follows: 1- By checking the dip switches, I found that the end of digital outputs is QB39 (located at central rack). End of digital inputs IB89 (located at extension rack). 2- I connected online to the PLC, and from the menu "PLC" - Output PLC Memory, I entered the starting address F F000H. I found that starting from address F F05A and till the address F F07F the value is FFFF which means that this area is empty. Refer to the attached print out from the Comprofibus program, now I am confused which address I need to enter in the reserved Iarea for the master, and which address I have to enter for the address of the DP slave? Can you help me? Best regards Attachmentconfiguration.zip (207 Downloads) |
8/11/2009 2:12 AM | |
Joined: 10/7/2005 Last visit: 5/2/2024 Posts: 3004 Rating: (1046) |
"Nothing" is the short answer dear yac! All this "reserve address" does is to cause a warning if you try to use any "reserved" address areas for your DP Slaves, so leave it blank as you already know which addresses are in use in the central and expansion racks.
The addresses that you want to use for your ET200M I/O's. Note too the inbuilt help of COM Profibus which is quite comprehensive and useful. You'll also findthe COM Profibus manual on your COM-PB CD, nonetheless, below is the link for it and also another useful one relating to IM308C which I trust will come in handy. COM PROFIBUS ET 200 Distributed I/O System with IM 308-C I hope this helps |
Cheers |
|