7/27/2018 2:57 PM | |
Joined: 12/18/2014 Last visit: 6/2/2024 Posts: 33140 Rating: (4094)
|
Do you have in the settings of the TDE the IP address of the LOGO! Basic module set. This must done in the menu under the menu item "LOGO! Selection". See attached PDF file. AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 pages 355-357.pdf (304 Downloads) |
7/27/2018 3:06 PM | |
Posts: 15 Rating: (0) |
Yes the IP address is the same as the Logo. then when I go logo settings and switch to admin it wont let me |
7/27/2018 3:07 PM | |
Posts: 15 Rating: (0) |
On the logo BM its asking for the ADMIN password. Do you know what it is please? |
7/27/2018 3:15 PM | |
Posts: 15 Rating: (0) |
Yes that's exactly how they are. What I meant was that from the Logo TD I have selected to correct IP of the BM |
7/27/2018 3:17 PM | |
Posts: 15 Rating: (0) |
I tried LOGO but its invalid :( |
7/27/2018 3:22 PM | |
Joined: 12/18/2014 Last visit: 6/2/2024 Posts: 33140 Rating: (4094)
|
Where enter you the password? In the basis module or in the TDE? If you enter in the basis module and it was not accepted, then have you changed the password. On delivery status, the password is LOGO. AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 page 69.pdf (194 Downloads) |
Last edited by: ixo65 at: 7/27/2018 3:26:19 PM |
|
7/27/2018 3:26 PM | |
Posts: 15 Rating: (0) |
I am writing the password to the BM. The password has not been changed as this is a new BM. is there a reset function to reset to factory default pls? |
7/27/2018 3:30 PM | |
Joined: 12/18/2014 Last visit: 6/2/2024 Posts: 33140 Rating: (4094)
|
Under "Tools > Transfer > Factory reset LOGO!" |
7/27/2018 3:34 PM | |
Posts: 15 Rating: (0) |
Ok thanks now its in admin mode. How can I set Admin the TD? when I am going from the TD, Logo settings - Setup - Switch to Admin = Failed to submit |
7/27/2018 3:40 PM | |
Posts: 15 Rating: (0) |
The TD seems that is not communicating with the BM |
7/27/2018 4:22 PM | |
Joined: 12/18/2014 Last visit: 6/2/2024 Posts: 33140 Rating: (4094)
|
You can not upload anything to the TDE, only to a basis module. |
7/27/2018 4:56 PM | |
Posts: 15 Rating: (0) |
Yes I tried that aswell. Sorry but I still cannot manage to communicate. Thanks for your help |
7/31/2018 7:05 AM | |
Joined: 2/20/2014 Last visit: 5/9/2024 Posts: 395 Rating: (38) |
Hi pompagarage, If you are expecting a proper solution, it is better for you to upload the file (if you are not ready to upload actual program file, then please proceed to create another separate program file (just with one or two lines of circuit program) & configure the message text to be displayed on both base module & TDE (can you also provide the photo of the IP setting done on the base module & TDE (to capture & upload a photo will not take a very long time). Please appreciate that ixo65 is taking all his time replying to your every post & after so many posts you are not taking the effort to provide any program file.screenshots/photos. This is not the right way to repeatedly post your query without providing the full information requested by the person who is volunteering to support you. |