6/5/2013 7:27 PM | |
Posts: 49 Rating: (0) |
Hiiiiiiiiii you can use barrier signal and connect your analoge signal to this barrier and take the output signal from this barrier to PLC. |
6/6/2013 7:06 AM | |
Posts: 49 Rating: (1) |
Dearahmed_abdelhady Please suggest barrier. So that we can install and take trials
|
6/6/2013 8:00 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (713)
|
Hello, If it comes to signal converters/isolators i like to use Phoenix because the wide range of solutions. First you can try some more things, try to isolate the CPU power supply 0V from ground, if not possible try it at the sensor/ transmitter side. Make sure that unused analog inputs are bridged. (between B+ and B-) Do you have a drawing of how things are connected and some documentation of the sensor/ transmitter? Regards, Marcjan |
Problem solved? |
|
6/6/2013 10:09 AM | |
Posts: 49 Rating: (0) |
Hiiii Yutong instrument TM6700 |