7/19/2018 6:15 PM | |
Joined: 7/7/2010 Last visit: 6/4/2024 Posts: 14766 Rating: (2377)
|
Since you have the original PLC program, if you sort the PLC tags to get the inputs / outputs sorted, you can quickly capture telegram data, and then associate it with a slave device. Go online with the devices using TIA Portal to see what you can see via online access via a profibus adapter on your TIA portal laptop. At least you can see all the device addresses, the PB configuration, and possibly more. This must be the expensive option (or similar) you mentioned: https://eandm.com/ExtraContent/Products/Content/Autem_Profibus.aspx How many slaves are being swapped?
|
science guy |
|
This contribution was helpful to1 thankful Users |
7/19/2018 6:35 PM | |
Joined: 3/16/2015 Last visit: 10/10/2021 Posts: 1250 Rating: (173) |
Thanks Huggy, I'm replacing two out of six. I know the slave addresses as I can see the setting on the hardware. |
7/19/2018 10:10 PM | |
Joined: 3/16/2015 Last visit: 10/10/2021 Posts: 1250 Rating: (173) |
This is so simple it's brilliant. |
This contribution was helpful to1 thankful Users |