6/5/2009 10:12 AM | |
Posts: 382 Rating: (47) |
Dear Abyrne, The probelm could have come from yourwiring You may want to try this out:- 1]disconnect all output wiring and left with the supply wiring to the SM422. 2] Then connect back the wiring one by one to the card channel and measure see which one gives you the residual voltage. Hope this helps. with regards, how come? |
This contribution was helpful to1 thankful Users |
6/5/2009 11:43 AM | |
Joined: 5/28/2008 Last visit: 5/29/2024 Posts: 4507 Rating: (837) |
Hello Abyrne, |
Last edited by: Ayman Elotaify at: 6/5/2009 11:43 AMAyman Elotaify |
|
This contribution was helpful to1 thankful Users |
6/6/2009 7:29 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (307) |
Hello, In the technical sheet of the SM422 you see that even with a "0" status, the board may deliver a residual current of 0.5 mA. I believe that if you connect only a very high impedance (like a voltmeter where the input resistancemust be very high, several MegOhms) you could measure a high voltage. If you conenct like you did a usual consumer (whichhas only a fewhundreds of Ohm or less), themeasured voltage drops. |
Best regards |
|
This contribution was helpful to1 thankful Users |