5/24/2022 5:13 PM | |
Joined: 12/18/2014 Last visit: 9/13/2024 Posts: 33766 Rating: (4192)
|
Then delete Q3 and the other blocks to this function if you mean you don't need it. |
5/24/2022 5:19 PM | |
Joined: 9/7/2021 Last visit: 10/18/2023 Posts: 52 Rating: (0) |
I will review. Once again thank you so much for helping me to solve the problem. Thank you. |
5/24/2022 5:33 PM | |
Joined: 9/7/2021 Last visit: 10/18/2023 Posts: 52 Rating: (0) |
If you have a better idea please post it so I can build on it and develop further. Thank you. |
5/25/2022 4:14 AM | |
Joined: 9/7/2021 Last visit: 10/18/2023 Posts: 52 Rating: (0) |
Hi Ixo65. With version V7 is there a way to control the two pumps to run so that their time is equal. |
5/26/2022 6:35 AM | |
Joined: 12/18/2014 Last visit: 9/13/2024 Posts: 33766 Rating: (4192)
|
Here version 8. The program compares via a UDF the operation hours of the two pumps by using two hour counters. If the operation hours of pump 2 are greater to the operation hours of pump 1, then is pump 1 the priory pump. AttachmentAlternationTest_V8.zip (568 Downloads) |
This contribution was helpful to1 thankful Users |
Follow us on