7/7/2013 9:01 AM | |
Joined: 5/28/2008 Last visit: 6/10/2024 Posts: 4509 Rating: (837)
|
Hello, I am agree withVithani. It is possible but not recommended. As the output waveform won't be pure sine wave. it will contain a lot of harmoncs. And it may be harful for your loads. (By the way, what are loads you want to fed for thjis application?) Why do not you use an isolating Variable transoformer?
|
Ayman Elotaify |
|
7/7/2013 9:35 AM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating: (477)
|
Search some more options. I dont think its a good idea May beisolating Variable transoformer as suggested by Ayman Elotaifyor any other voltage regulators will be good and mostly that will be cheaper than buyinga VFD |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/8/2013 4:28 PM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating: (477)
|
Well sehgal I still feel this will be costlier option Here i have one dcoument on Transformer at output - it is for Motor control but you will get some idea what precautions you will need Regards, Devesh Vithani Attachmenttransformer at output.pdf (288 Downloads) |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/11/2013 8:19 AM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating: (477)
|
Dear jeet2907 VFDCAN work but SHOULD NOT be used Please read all replies and you will get idea how it can work Regards Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/13/2013 10:35 AM | |
Joined: 3/17/2013 Last visit: 6/9/2024 Posts: 481 Rating: (43) |
Variac : I was always thinking of manual dimmer stat. Mistake from my side Regards, Vijay |