12/9/2020 10:56 AM | |
Joined: 8/29/2019 Last visit: 4/24/2024 Posts: 33 Rating:
|
Hello, any news on the event "System initiated session termination" 16# 02:4427? |
3/23/2023 12:06 PM | |
Joined: 8/3/2009 Last visit: 6/14/2024 Posts: 13030 Rating:
|
Hello Simousss85 The Error means that the HMI has terminated the connection (not the PLC) -> If you cannot get the connection work at all then an issue could be this: https://support.industry.siemens.com/cs/ww/en/view/109803668 If the connection works and randomly disconnects with this error then it could also be that the Panel is in an overload and cannot handle the communication again... -> Does it work after a reboot? which Image Version do you use on the Panel? FW version of the PLC? TIA Version ? Bye Murof |
Last edited by: Murof at: 03/23/2023 12:06:46If this Information really helps, you could use the Rate function |
|
5/11/2024 8:00 AM | |
Joined: 8/29/2013 Last visit: 5/11/2024 Posts: 1 Rating:
|
XLLS. Hola, también fue ajustar la hora en la pantalla Comfort y ya comenzó a leer y desapareció el fallo. |
5/13/2024 9:13 AM | |
Joined: 6/19/2017 Last visit: 6/12/2024 Posts: 8140 Rating:
|
Hello XLLS, thank you for sharing your answer For the next time, please try to discuss in English language. This is an international community, and we try to focus on one language. This is the translation of your post: