7/5/2014 6:15 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear All, I would like to take this opportunity and provide you with the fruits of my software development on Modbus RTU Master Communication function blocks over the past years. The function blocks are running on S7-300, S7-400 and S7-400H CPU’s and do not require any additional hardware dongle to be purchased and inserted into the communication processor module. I tried to develop these function blocks from a user perspective in order to make its use as easy as possible for the programmer. Multiple requests to more than one slave connected to the communication processor in a daisy-chain/multi-drop network can be configured within no time. The following SIMATIC S7 communication processors are supported:
GENERAL INFORMATION & SUPPORT For installation, connection and interface configuration of your communication processor module kindly follow its respective documentation. I also advise you to take some time and go through the general information about Modbus provided by our forum member smiffy. Especially if you are a beginner in Modbus, seek for support or just want to learn more about it. This software driver is running on several plants in the oil and gas industrysince many years without any known issues. In case you face any problem with the provided function blocks place a comment here in the forum and I will try to give you support. Additionally I would appreciate if users who have already successfully implemented the communication driver into their project will support me in that. I hope tomake your life a bit easier with this development.
With Best Regards NEW ! LINKFOR MODBUS RTU SLAVE DRIVER MODBUS RTU MASTER DRIVER DOWNLOAD (ATTACHMENTS) The attached program files need to be retrieved within the SIMATIC Manager. Currently there is only one manualfor theCP340version but the others are all working in the same way just with different function blocks. MBMA340.PDF - Manual for Modbus RTU Master for CP340 MBMA340.ZIP -Example projectfor Modbus RTU Master driver for CP340 MBMA341.ZIP -Libraryfor the Modbus RTU Master driver for CP341 MBMA441.ZIP -Libraryfor the Modbus RTU Master driver for CP441-X MANUAL MBMA340 AttachmentMBMA340.pdf (5983 Downloads) |
Last edited by: TIBI68 at: 9/16/2014 11:52 AMLast edited by: TIBI68 at: 7/6/2014 10:41 AMMBMA441.ZIP download added Last edited by: TIBI68 at: 7/5/2014 6:28 PMLast edited by: TIBI68 at: 7/5/2014 6:26 PMGive us your feedback and show us your respect! |
|
This contribution was helpful to78 thankful Users
|
7/5/2014 6:17 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
MBMA340
AttachmentMBMA340.zip (3921 Downloads) |
Give us your feedback and show us your respect! |
|
This contribution was helpful to18 thankful Users |
7/5/2014 6:18 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
MBMA341
AttachmentMBMA341.zip (4412 Downloads) |
Last edited by: TIBI68 at: 7/6/2014 10:36 AMStatus W#16#EEEE removed Give us your feedback and show us your respect! |
|
This contribution was helpful to25 thankful Users |
7/5/2014 6:18 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
MBMA441 AttachmentMBMA441.zip (2230 Downloads) |
Last edited by: TIBI68 at: 7/6/2014 10:37 AMDownload file added Give us your feedback and show us your respect! |
|
This contribution was helpful to10 thankful Users |
7/7/2014 10:27 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Pero51 ,
The MBMA340.ZIP file is a project example showing how all functions work. The MBMA340 function block executes allMBMAREQfunctions sequencially.Writing a single register on trigger is not implemented.Could be maybe inlater version.
The LINK parameter has no function itself but is required for the data exchange between the two blocks. RegardingDONE and ERROR outputs: Isfor indication when the data is completly received or transferred. You just simply call the MBMAREQ blocks one after the other in your program. Is also described this way in the manual.
A trigger was neverplannedwhile, tobe honest, I never required it.Maybe there are some applications where a trigger functionwould be nice, but whatthen you will need to handle transmission failures manually (i.e. resending the requests). A cyclic executiondoes not giveyou that trouble. In case you wantto execute the requests only every x-Seconds you can place the MBMA340 block in an interrupt OB. Thanks for your valuable input and ideas. I will keep it for further developments. Best Regards. |
Give us your feedback and show us your respect! |
|
7/8/2014 7:56 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Pero51 ,
The MBMA340 does not call the MBMAREQ function block. The MBMAREQ blocks writesits requestsinto the instance of the MBMA340block if there is no other request already running.
The MBMAREQ block writes the complete modbus request message, except the CRC, and the S7ADDR into the instance of MBMA340. The MBMA340calculate the CRC, sends the complete modbus frame with P_SEND and waits for a reply with P_RCV.Pending on the telegram received it transfer the received data into the S7ADDR andwrites theSTATUS, DONE and ERROR outputs.
The user needs a wayto define somehowthe modbus requestsand I believethis is the easiest, esspecially for beginners.
The MBMAREQ needs its unique instance data block. The LINK needs to be the same, otherwise the MBMAREQ is not able to transferhis request data into the instance of MBMA340. This LINK parameter is the only way the two blocks can communicate with eachother. They need to be same! Most users skip reading manuals.I spent alot of time making itand it is worth reading it. Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/15/2014 1:58 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling, I try to avoid working with TIA whenever I can Are you able to migrate the MBMA340.ZIP project into your TIA? If yes, send me a PM with your email and I will send you the archive. Better you get your Step7 V5.5 up and running. Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/15/2014 3:03 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling , you will shortly receive the file to your email. Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/15/2014 3:27 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling , the files have been sent to your email. I am happy for any feedback and maybe you can shareyour experience with us. Best Regards. |
Give us your feedback and show us your respect! |
|
7/16/2014 10:54 AM | |
Joined: 1/17/2007 Last visit: 5/8/2024 Posts: 1542 Rating: (532)
|
Yeah, I agree the CRC is incorrect. For the message 01 03 10 00 00 05 the CRC should be 81 09. You can check the CRC calculation here:- http://www.lammertbies.nl/comm/info/crc-calculation.html TIBI68, if you want a proven CRC calculation algorithm, I can provide you with one, or you can PM me your CRC calculation code and I can check it for you. Regards, Smiffy. |
Programming today is the race between software engineers building bigger and better idiot proof programs, and the universe producing bigger and better idiots. |
|
7/16/2014 11:09 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Thanks for your feedback Hopling, Nobody is perfect I must have sent you the wrong file. Give me some time. I will come back to you soon. Best Regards. |
Give us your feedback and show us your respect! |
|
7/16/2014 11:12 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Thanks smiffy, my calculation is working, however I must havecompiled himan old block. Thanks for your offer Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/16/2014 1:15 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling , I checked the CRC calculation of the block and it is giving me "81 09" which is correct. Now we will need to find out why it sends wrong CRC "01 09". I dont have TIA can you print your program in PDF and upload or send it to my email? Thanks. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/16/2014 1:40 PM | |
Posts: 24 Rating: (1) |
Just sent it, hope for your help... |
7/16/2014 2:04 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling , I cannot open you project correctly in my version. Kindly check the following parameters in theprotocol section of your CP. Transmission Rate: sameas atslave Data Bits: 8 Stop Bits: 1 Parity: same as at slave I see data bits 7 in your configuration. Change, tryand update me. Good luck! |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/16/2014 2:56 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Alhamdulillah Hopling , I am very happy that it works now for you. It would be interesting to know if it is going to work after migrationto TIA as well. Actually theseparametersare a very good point to mention in the manual for other users. Thanks. |
Give us your feedback and show us your respect! |
|
7/16/2014 3:19 PM | |
Posts: 24 Rating: (1) |
I just migrated it to TIA without any problems... It's working as good as it worked while using STEP7 V5.5! |
This contribution was helpful to1 thankful Users |
7/17/2014 11:54 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Bryll,
Useful for users is not always useful for vendors. I hopeone day Siemenswill provide us with a freesolution like for the new PLC's.
Yes pleaseand provide us with your feedback!
I have noplan forit at the moment. Im currently working on transferring myModbus-TCP Client(code from 2003) from STL to SCL. When I am done and have tested it I will share it as well.
Good idea? That dependsfor whom. Best Regards. |
Give us your feedback and show us your respect! |
|
7/18/2014 9:21 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling,
I never needed a modbus rtu slave in my projects only masters. That's the reason there is no slave driver existing from me.
Your "positive feedback" is my reward, thanks.
I am sure that there issome very good user written code out there but these usersare not willing to share their "hard work" with us. Best Regards. |
Give us your feedback and show us your respect! |
|
7/18/2014 11:15 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling, the driver does not support reading/writingon trigger! If there would be atriggerthe user would need to control the sequence by himself. I took this headache from the userby executing all requestssequentially and headache free. There is an advantage of cyclic transmission. In case of a transmission failure the values are written in the next cycle. This is not thecase when you write on trigger unless you handle it by yourself. I know, you lose a bit performance. What is your CPU cycle time with all 4 requests? Best Regards. |
Last edited by: TIBI68 at: 7/18/2014 11:35 AMLast edited by: TIBI68 at: 7/18/2014 11:33 AMGive us your feedback and show us your respect! |
|
7/18/2014 12:04 PM | |
Posts: 24 Rating: (1) |
del |
Last edited by: Hopling at: 7/18/2014 12:05 PM |
|
7/18/2014 12:39 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling , this is just an idea and not tested but you can give it a try. At the write request blocks you use a free flag bit (trigger bit) on EN input and reset it withDONE or ERRORoutputs fromthat request block. I think you got what I mean From the var table you can set the trigger bit to check it out. Let me know your results. Best Regards. I forgot to mention that you will nee individual DONE and ERROR bits as well. |
Last edited by: TIBI68 at: 7/18/2014 12:44 PMGive us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
7/18/2014 1:40 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Hopling, I was very exitedso I check it out myself It works great for me as well! Thanks for your support! Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
8/11/2014 1:25 PM | |
Posts: 5 Rating: (0) |
FB8 (R_TRIG: Detection of the rising edge ) is Already present in the library , and we cant change the FB number of your block.?? |
8/11/2014 2:10 PM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear HamidShiakh, thanks for your comment. You are free to use Loadable Modbus Master RTU driver from Siemens instead. Let me know If youneedtheSiemens order number. Best Regards. |
Last edited by: TIBI68 at: 8/11/2014 2:11 PMGive us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |
8/14/2014 9:24 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Good Job Baron, try to change the S7ADDR to DB11 DBX0.0 BYTE 1. The simulator has a "Monitor" option to see the traffic. Kindly send me a snapshotof that traffic window. No problem we will get it work! Best Regards. |
Give us your feedback and show us your respect! |
|
8/14/2014 9:46 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Baron, I sent you a PM. Best Regards. |
Give us your feedback and show us your respect! |
|
8/14/2014 11:43 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear Baron, I sent you a PM. Best Regards. |
Give us your feedback and show us your respect! |
|
9/11/2014 9:56 AM | |
Posts: 9 Rating: (0) |
Dear All, I program Modbus RTU with hardware: - CPU 313C-2DP. - CP 341 (Without Dongle). - Multimeter (RS485-Modbus RTU). I use library of "TIBI68". Software online same picture attach. But CPU 313C-2DP not SEND or REC data. CP341 RX&TX led not flash. Help me please!
|
9/11/2014 10:35 AM | |
Joined: 12/1/2009 Last visit: 5/22/2024 Posts: 672 Rating: (147) |
Dear AchutVn2T , thanks for using the library. I sent you a PM. Don't worry I will help you. Best Regards. |
Give us your feedback and show us your respect! |
|
This contribution was helpful to1 thankful Users |