(0)| 5/26/2020 1:05 PM | |
Joined: 5/10/2017 Last visit: 12/18/2025 Posts: 5 Rating:
Hello Vishakha, I'm currently using DT50 on some of my equipment. I use it for positioning but the accuracy is not good enough (+-1mm noise because of analog signal). I wonder if switching to IO link improves this accuracy? If not I'll have to revamp the system to have encoder in combination with drive-cliq to position the equipment. Current setup: DT50 to AI on ET200SP, PLC S7-1517 reads AI signal and sends speed setpoint to drive. ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 05/26/2020 13:36:37New subject after splitting |
| 5/28/2020 12:44 PM | |
Joined: 9/21/2012 Last visit: 1/17/2026 Posts: 4850 Rating:
With IO-Link you can have an accuracy of +/-0.1mm. |
| 5/28/2020 2:23 PM | |
Joined: 7/7/2010 Last visit: 1/16/2026 Posts: 16379 Rating:
If your position feedback analog signal is noisy, what do you imagine is happening to every other analog signal? If you have 3-wire analog devices, you may need galvanic isolators (signal conditioners), and may even need to up-size the 0V wire to all your 0V distribution terminal groups, and especially any that run between the voltage source and any remote IO panels. I found great improvements by increasing the 0V wire size by 2 standard sizes when I use 3-wire analog devices. If you can use 0-20 or 4-20mA analog signals, you are much better off. Even if the analog input is voltage, you can insert the proper resistor at the input terminals to get proper and less noisy analog inputs. I guess what I'm saying is, you can use the IO link as your "galvanic isolator", which is a lot of effort to disguise a system-wide problem for a single input.
science guy |