7/27/2021 9:54 AM | |
Joined: 12/19/2017 Last visit: 6/23/2022 Posts: 5 Rating: (0) |
Greetings of the day Hi, V20 drive modbus communication done as per the below, Step1: Assign Drive parameters and modbus macros as per the manual (Refer the drive manual) Step2: Send the drive ON/OFF and write frequency set point command as follows. OFF Command: Write 047E hex [1150 dec] to the modbus address: 40100 - STW Frequency setpoint: Write Raw value - 0 to 16384 which is equals to 0-50Hz to the modbus address: 40101 - HSW ON Command: Write 047F hex [1151 dec] to the modbus address: 40100 - STW
AttachmentSinamics_V20 Hz Scaling.pdf (377 Downloads) |