You explain your problem too broadly. Which website are you talking about? How is your signal? |
9/14/2021 7:26 AM | |
Joined: 5/19/2021 Last visit: 10/21/2024 Posts: 19 Rating: (0) |
thank you for your answers. I'm sorry for the description of the problem. My English is very bad. also, I send you an example file of what I did. The user can put a selector button to put a pump in automatic mode. if there is a power cut, this selector returns to 0.... And the process don t resart . many thanks Attachmentretentivitybit.zip (266 Downloads) |
9/14/2021 8:01 AM | |
Joined: 12/18/2014 Last visit: 10/21/2024 Posts: 34006 Rating: (4229)
|
Hello PaulFaud, the problem is that the VM area has no retentivity. In attachment a possible solution. I added a push button with transparent images for On and Off and give them the address V101.5. Then I place the push button over the switch button (same coordinates). The switch button has now the address M1. In the LOGO! program I toogle a pulse relay (B001). By this block you set the retentivity. The output of B001 is connected to the flag M1. Attachmentretentivitybit_V2.zip (277 Downloads) |