Industry Online Support
Technical Forum
3/28/2009 3:50 PM | |
Joined: 9/28/2005 Last visit: 3/12/2024 Posts: 2957 Rating: (242) |
Yes you wrong . dchartier suggestion is very useful for you, but basically what it does I wrote you in the first post. So you don't need to wait for an input, but for example if your scan cycle is 1ms and DI filter is 6ms, so you will "see" this input as logical "1" only after 6 program scans. Its other story with analog. You will allways see average of analog value for filter time. If your filter is 6ms for analog so you will see average value for 6ms of analog input. Thats all. You will read your values every scan cycle, but they will change not every cycle. |
Best regards, |
|
3/28/2009 6:03 PM | |
Posts: 14 Rating: (0) |
Thank You Daniel & DariusYou Realy Helped ,I Got It(Y)(Y)(Y) |