Joined: 9/22/2020 Last visit: 4/25/2024 Posts: 9 Rating: (0) |
hi dears how can I use bit memory about analog input wire broken diagnostics ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/14/2022 07:06:13New subject after splitting |
|
3/13/2022 6:12 PM | |
Joined: 9/27/2006 Last visit: 10/9/2024 Posts: 12285 Rating: (2685) |
Hello M. Vadigard; Are you thinking of using a S7-1200 PLC, as this thread refers to? The mechanism for detection and diagnostics of wire break in S7 PLCs is the diagnostic error interrupt, OB 82. See the description in this section of the S7-1200 programmable contoller manual: https://support.industry.siemens.com/cs/ww/en/view/109478121/70491858187 This next document will show you the steps required to enable the wire break detection and evaluate it in OB 82; the example uses an analog output module, but the same reasoning applies to an analog input module: https://support.industry.siemens.com/cs/ww/en/view/42320122 Hope this helps, Daniel Chartier |