Hello Kashir Its also a matter of amount of data. if you want to log almost one Tag in 20ms cycle then you have in one hour 180.000 Values.... how long do you want to store so much data? (only for a short amount of a few seconds or minutes?) A Comfort Panel (for example TP1200) has only 20.000 values per log and a Advanced RT 500.000 values per log. And also as mentioned the minimum logging cycle for continious logging is 1second. In WinCC V7.X and WinCC Professional you have a SQL Server database with much more power but the minimum loggin cycle is about 500ms. But there are also solutions for faster logging (LINK) but not for S71200. you can have also a look ath the datalogs for S71200? (LINK) Bye Murof |
Last edited by: Murof at: 03/25/2022 09:15:31If this Information really helps, you could use the Rate function |
|