6/30/2022 9:31 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684)
|
Hello; The information you need is presented in the following document: _ How do you configure a fault-tolerant S7 connection for a user application via Industrial Ethernet with the SIMATIC NET PC software? https://support.industry.siemens.com/cs/za/en/view/16667714 “Fault-tolerant S7 connections are only available with a CP1613 and a CP1623. The use of a normal network adapter is not possible. Furthermore you need the license for the SIMATIC NET PC software S7- REDCONNECT on the PC station, which communicates with the S7400-H system over fault-tolerant S7 connections.” S7-Redonnect license: 6GK1716-0HB16-0AA0 HARDNET-IE S7 REDCONNECT V16 including OPC server and HARDNET IE-S7 software for fail-safe S7 communication; floating license; R-SW, software + electrical manual on DVD, license key on USB stick, class A 2 languages (de, en); for Windows 7 SP1 Professional/Enterprise/Ultimat e (64 bit); Windows® 10 Professional/Enterprise (all 64 bit) version 1809, 1903; Windows® Server 2012 R2 Update (Standard Edition); Windows® Server 2016 (Standard Edition, Datacenter); Windows® Server 2019 (Standard Edition, Enterprise) . You could also look at Ch. 14.6 in the S7-400H v6.0 manual, "Communication via fault-tolerant S7 connections". https://support.industry.siemens.com/cs/za/en/view/82478488 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 06/30/2022 21:42:16 |
|