Hi cusco, With a centralized configuration of the IO-modules, a CPU stop is the defined system behavior when a module fails, or a fault is detected on the central backplane bus. This behavior has been implemented intentionally in the S7-1500 system to prevent the CPU from further processing of undefined values. Independent of this behavior It´s recommended to check the use of ET 200MP with the active backplanebus for applications with a high demand of availability as a more appropriate solution. https://support.industry.siemens.com/cs/ww/en/view/109781570 |