Hello everyone I'm using the 6ES7 136-6BA00-0CA0 card in my project. But I'm not getting the inputs in the PLC. When I checked the hardware diagnostics everything is healthy (no passivation). But there is a T QBAD = 1 and Pass_OUT = 1 in the respective F DB. I'm also experiencing the same thing with my 6AV3 688-3AF37-0AX0 panel also. The QBAD error is not even resetting when I try to acknowledge I have attached some screenshots for reference AttachmentQBAD ERROR.docx (596 Downloads) |
9/2/2022 7:25 AM | |
Joined: 5/30/2022 Last visit: 6/26/2024 Posts: 537 Rating:
|
Hi Amar vaidya14, I recommend you review the following manual: SIMATIC Industrial Software SIMATIC Safety - Configuring and Programming And also this: QBAD/PASS_OUT/DISABLED/QBAD_I_xx/QBAD_O_xx and value status Note For F-I/O with outputs, acknowledgment after F-I/O or channel faults may only be possible some minutes after the fault has been eliminated, until the necessary test signal is applied (seeF-I/O manuals). |
If this information really helps, you could use the Rate function. |
|
10/14/2022 3:18 AM | |
Joined: 2/11/2021 Last visit: 2/16/2023 Posts: 4 Rating:
|
Hey everyone I'm facing the same problem. Did you find a sollution for this? |
10/19/2022 3:33 PM | |
Joined: 2/11/2021 Last visit: 2/16/2023 Posts: 4 Rating:
|
Thank you for your answer! Eventually fixed it by actually using it in the safety program. |