Hi Mehul_1982, When the drivers are not generated automatically when compiling, it is most likely that the module is not released for your PCS7 version, which you can verify in the following manual: SIMATIC Process Control System PCS 7 Released modules (V9.0) In case the module is not released, it does not mean that it cannot be used. It can be used without problem, but you have to do the programming and interconnections of the block manually. |