Hi, Normally the feature bits are used to parametrize instances so instance specific changes. You would set the correct feature bits at the block. The same applies for the OS permissions...A valve X can be opened by the operator but valve Y cannot. You can modify the behavior instance specific. You can enable/disable the bits by double clicking the Feature signal and select the correct bit. You can even do this during test mode. But as of PCS7 V9.0 SP1, the AP library features two new blocks: "StrctCom" (Structure composer) and "StrctDeC" (Structure decomposer) to connect to the Feature and OS_Perm signals. So, you can parameterize the bits at the input side, connect the block to the "Feature" signal of the technological block and then you're done.
|