Hi, Thank you for the response. Unfortunately the builder has locked out the PLC. |
11/29/2022 11:50 AM | |
Joined: 10/17/2007 Last visit: 9/17/2024 Posts: 4031 Rating: (353)
|
Let's say M07 for Hi pressure coolant on and M09 is shut it off PLC program can be like this FC107 A DB21.DBX194.7 // M07 code S Q20.7 // free output for Hi pressure coolant A DB21.DBX195.1 // M09 code R Q20.7 attached page for M code--very easy for programmer if you think that helps you, can you please rate my answer AttachmentM_function_list.pdf (560 Downloads) |