Great day Everyone, I'm currently working on connecting LOGO8 to TM221 to read data of Logo, When I modscan the LOGO8, I can open connection using port510, is there any way I can change it to 502? because my TM221 plc accepts only 502 port channel. Please see attached Ethernet Setting ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/20/2023 05:03:12New subject after splitting |
|
1/20/2023 5:44 AM | |
Joined: 12/18/2014 Last visit: 9/24/2024 Posts: 33827 Rating: (4203)
|
Have you with the LOGO! connection only to the TM221? Please can you upload your LSC diagram as a ZIP file? |
1/20/2023 6:17 AM | |
Joined: 10/1/2022 Last visit: 7/31/2024 Posts: 3 Rating: (0) |
Hi ixo65 Please see attached file for your reference AttachmentADC2_V2.4_MC_1.zip (357 Downloads) |
1/21/2023 2:13 PM | |
Joined: 12/18/2014 Last visit: 9/24/2024 Posts: 33827 Rating: (4203)
|
LOGO! Reserves ports 502 to 509 for the 8 static Modbus server connections on Modbus. |