2/11/2023 1:52 PM | |
Joined: 8/21/2022 Last visit: 3/24/2024 Posts: 4 Rating: (0) |
Hello, How I can show in scada plc power on off status. I can usePlc- S7-200 smart and WinCC RT Advance V15.1 SCADA . Please suggest me. ------------------------------------------------------------------------------------------ |
Last edited by: vaibhav489 at: 02/11/2023 13:52:44Last edited by: Jen_Moderator at: 02/13/2023 05:26:32New subject after splitting |
|
2/16/2023 11:33 AM | |
Joined: 8/3/2009 Last visit: 11/19/2024 Posts: 14193 Rating: (1775)
|
Hello the S7200 has not much options for this. for S712001500 you can read it out. With S7200 you only can use the Systemalarms for disconnecting. Or a simple way would be to dynamise a toggle tag from the PLC to let a circle or similar change from on to another colour every 1 or 2 seconds. Then you can see if the flashing stops you do not have a connection. if a head line or somilar this little optical thing should give you a fast response for this issue. Here the FAQ for other PLCs: https://support.industry.siemens.com/cs/de/en /view/109481628 Bye Murof |
Last edited by: Murof at: 02/16/2023 11:33:48If this Information really helps, you could use the Rate function |
|
This contribution was helpful to1 thankful Users |