Hi Mario Braganca, |
5/21/2009 4:27 AM | |
Joined: 9/27/2006 Last visit: 10/17/2024 Posts: 12289 Rating: (2687) |
Hello BRL; If you look at the informationfor Sentron on the SE&A pages (Siemens United States, Power Distribution) it shows that Sentron PAC3200 supports TCP/IP (SEABus protocol) and Modbus-TCP on its in-built Ethernet port. http://www2.sea.siemens.com/Products/PowerDistribution/Product/ACCESS-Power-Monitoring/Product/Sentron+PAC3200.htm I don't know much about SEABus, but Modbus/TCP is accessible over Ethernet CPs on the S7-300 and S7-400 CPUs; that would make it a very simple setup for you. The following link will show you how to use the blocks fron "Open Modbus/TCP" to link a S7 CP to a third-party partner. http://support.automation.siemens.com/WW/view/en/22660304 Hope this helps, Daniel Chartier |