Hi, The hardware signals can be assigned to a PIP. The signals are read in according to the interrupt OB. In CFC you insert blocks also used in an interrupt OB. If they don't match, you can get problems. For example: If you have a totalizer puls which is used in 500ms but the Totalizer is used in CFC interrupt 1sec. then 50% of the pulses are not counted. Thats why they should be equal |