Hello Múrof, Using WinCC RT Professional, after I have set up a Data logs and worked with the project loaded on a PC station, how can I access the database to see the values of the registered logging tags? I am not able to find any information about this. Thanks in advance
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/19/2023 12:32:01New subject after splitting Last edited by: Jen_Moderator at: 06/19/2023 12:32:40Quote inserted. |
|
6/19/2023 2:26 PM | |
Joined: 4/8/2021 Last visit: 5/14/2024 Posts: 638 Rating: (101) |
Hi Erm2222_ As far as I know you can do that by using the WinCC OLE DB. Here you can find more information about how to do it: https://support.industry.siemens.com/cs/ww/en/view/109798671/39129326731 Hope you find it useful. |
Best regards, |
|
6/23/2023 9:57 AM | |
Joined: 8/3/2009 Last visit: 5/17/2024 Posts: 12970 Rating: (1650)
|
Hello erm2222_ If you just want to view the logged values then use a Tablecontrol or a Trend Control in sour WInCC Prof Runtime. If you want to read out the values from an external application then can use the Runtime API: https://support.industry.siemens.com/cs/ww/en/view/109813306/143300782219 But you cannot look just inside the SQL Table because the Taglogging DAta is stored comressed Bye Murof |