9/14/2023 8:56 AM | |
Joined: 10/22/2008 Last visit: 5/28/2024 Posts: 366 Rating: (5) |
Hello experts, I am looking for information about port/services that should be allowed for WinCC Professional V17 RT to communicate with S7-1500, and same time block Tia portal engineering. I found: https://support.industry.siemens.com/cs/de/en/view/8970169 But cannot see any clear information what port is used by TIA portal. In my case some VLANs should be enabled for service laptops but not all of them. I am really appreciate for any information. Best regards |
Last edited by: Oscar_83PL at: 09/14/2023 08:57:50Last edited by: Jen_Moderator at: 09/14/2023 11:47:46Link optimized. |
|
9/15/2023 11:22 AM | |
Joined: 7/19/2022 Last visit: 5/28/2024 Posts: 358 Rating: (61) |
Hello Oscar_83PL, In the same link that you specify there is a list of the ports at the engineering level that are used in the TIA Portal by the HMI: Which ports are used by SIMATIC WinCC Basic/Advanced/Professional (Engineering), WinCC Runtime Advanced/Professional, HMI Panels and IPCs? in and at a general level, documentation on the safety of a plant: All-round protection with Industrial Security - Plant Security |
If this Information really helps, you could use the Rate function |
|