Hi, Currently, I'm setting up a PCS7 system with ES, one OS server, and one OS client. I can download the project to both the OS Server and the OS Client. However, I can see the OS server system and Client system name in the list of accessible devices. But while configuring the OS server and client from " PLC >> Configure " I'm getting "Target computer is not accessible ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 12/15/2023 11:58:18New subject after splitting and Text formatting optimized Last edited by: AutoGen_6615511 at: 12/15/2023 12:08:34Last edited by: AutoGen_6615511 at: 12/18/2023 05:07:09 |
|
12/15/2023 1:09 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (927)
|
Hi, First, make sure that you are working on the ES station where the project is located. Make sure the name of the PC stations are entered in the SIMATIC PC configuration and set checkmark: Computer name identical to PC station name. Make sure that the PG/PC interfaces of stations are set to PC Internal. Note: The client is not configured via Configuration Console because it has no plant bus. Make sure you load the station configuration of the ES first (PLC->Configure, PLC->Download), otherwise the ES does not know the other stations. |
If I could help you, you can use the RATE button. Thank you. |
|