6/4/2019 2:38 PM | |
Joined: 9/27/2006 Last visit: 4/27/2024 Posts: 12257 Rating: (2665) |
Hello Anshul_Tiwari; With PCS 7 (which does not support the S7-1500 R/H CPUs) you can setup ET 200SP HA modules in a redundant I/O configuration. You cannot configure redundant ET 200SP or ET 200MP I/O with a S7-1500 R/H system. Refer to the following documentation: SIMATIC PCS 7 High Availability Process Control Systems (V9.0 SP1) https://support.industry.siemens.com/cs/us/en/view/109754977 SIMATIC S7-1500 S7-1500R/H redundant system https://support.industry.siemens.com/cs/us/en/view/109754833 In the last manual you will find various examples of redundant architectures for the S7-1500 R/H system. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 06/04/2019 14:40:42Last edited by: dchartier at: 06/04/2019 17:10:03 |
This contribution was helpful to1 thankful Users |
6/6/2019 8:03 AM | |
Joined: 7/13/2007 Last visit: 2/9/2024 Posts: 32 Rating: (1) |
Thanks Daniel for such exact clarification. |
2/22/2024 7:45 PM | |
Joined: 9/9/2021 Last visit: 2/23/2024 Posts: 6 Rating: (0) |
Is it Possible to use I/O Redundancy with S7-400H Controller and ET200SP I/Os.?? Regard, AJ